Posted - 28 Feb 2014 :  11:35:15  Show Profile Send D174812H a Private Message  Reply with Quote
Hi. Anyone give me some pointers for fitting a mains consumer unit please.

Mark Atkinson.

Relax..... Buy a boat!

merlin

United Kingdom
400 Posts

Posted - 28 Feb 2014 :  15:44:59  Show Profile  Visit merlin's Homepage Send merlin a Private Message  Reply with Quote
What do you need to know ?




Go to Top of Page

df

United Kingdom
5994 Posts

Posted - 28 Feb 2014 :  17:14:42  Show Profile  Visit df's Homepage Send df a Private Message  Reply with Quote
If it's on a boat DON'T use use twin + earth, use multi-stranded conductors to cope with vibration, soldered cable ends make for a more secure connection in screw clamps.




NBAS--The communal colostomy bag of the boating community.
Visit leomagill.co.uk
Go to Top of Page

D174812H

United Kingdom
69 Posts

Posted - 01 Mar 2014 :  01:44:37  Show Profile Send D174812H a Private Message  Reply with Quote
Merlin. We have a connection in the cockpit for shore power. This at present feeds one double socket in the cabin. I want to add more sockets, and thought it best to put them through a consumer unit. A friend on the marina feeds six sockets through a consumer unit. Just wondered if there was any special sort of stuff I needed to be aware of. His set up seems pretty simple.

Mark Atkinson.

Relax..... Buy a boat!

Edited by - D174812H on 01 Mar 2014 01:45:55
Go to Top of Page

merlin

United Kingdom
400 Posts

Posted - 01 Mar 2014 :  08:54:57  Show Profile  Visit merlin's Homepage Send merlin a Private Message  Reply with Quote
quote:
Originally posted by D174812H

Merlin. We have a connection in the cockpit for shore power. This at present feeds one double socket in the cabin. I want to add more sockets, and thought it best to put them through a consumer unit. A friend on the marina feeds six sockets through a consumer unit. Just wondered if there was any special sort of stuff I needed to be aware of. His set up seems pretty simple.

Mark Atkinson.

Relax..... Buy a boat!


How many sockets do hope to have Mark ?






Go to Top of Page

D174812H

United Kingdom
69 Posts

Posted - 02 Mar 2014 :  12:56:17  Show Profile Send D174812H a Private Message  Reply with Quote
Hi Merlin. Was thinking of adding another one or two. Maybe one in the cockpit and one at the other end of the cabin from the existing double socket.

Mark Atkinson.

Relax..... Buy a boat!
Go to Top of Page

merlin

United Kingdom
400 Posts

Posted - 02 Mar 2014 :  17:31:07  Show Profile  Visit merlin's Homepage Send merlin a Private Message  Reply with Quote
quote:
Originally posted by D174812H

Hi Merlin. Was thinking of adding another one or two. Maybe one in the cockpit and one at the other end of the cabin from the existing double socket.

Mark Atkinson.

Relax..... Buy a boat!



Hi Mark
as an Electrical Inspector I will try and not get to technical on
this type of installation

Firstly a consumer unit with an RCD is a must
you want one with an RCD rated at 30MA 40a if possible
but you may have to settle for a higher current rating say 80 or 100a
but it must still be 30MA (fault current)

next Circuit protection I would suggest for each socket (if wired on there own for ease of installation) a 10A MCB for each circuit
However you can loop two sockets together as a radial circuit from a 10A MCB

use 2.5 flex through out
from the shore supply socket to the consumer unit RCD (main switch)

then wire the socket circuits from the 10A MCBs Make sure the earths
are all securely tightened

Keep the install tidy, clip cables that can be seen
the BSS guys are getting more up to speed with mains electrics
I must admit some of the stuff that's out there is abysmal

don't crunch the numbers it doesn't work common sense prevails on
what you can use say 2.5Kw remember the shore supply may be 16A or
less

Once you are all connected test the RCD with the power on
making sure it disconnects the power on the boat

at the end of the day if you are unsure have it checked by a sparky
before you power it up




Go to Top of Page

df

United Kingdom
5994 Posts

Posted - 02 Mar 2014 :  17:50:27  Show Profile  Visit df's Homepage Send df a Private Message  Reply with Quote
quote:
I must admit some of the stuff that's out there is abysmal

You've seen mine then....
You can get 32A hookups on the broads.




NBAS--The communal colostomy bag of the boating community.
Visit leomagill.co.uk
Go to Top of Page

merlin

United Kingdom
400 Posts

Posted - 02 Mar 2014 :  19:30:32  Show Profile  Visit merlin's Homepage Send merlin a Private Message  Reply with Quote
quote:
Originally posted by df

quote:
I must admit some of the stuff that's out there is abysmal

You've seen mine then....
You can get 32A hookups on the broads.




NBAS--The communal colostomy bag of the boating community.
Visit leomagill.co.uk



32A is pretty good if there is one outlet on the pillar
there are plenty of 16A with four outlets on them so if everybody
puts the kettle on at the same time the lights go out

a 2.5mm shore cable is only good for just over 20Amps
and has to be no more than 25mtrs long